Oh boy, where do we even begin:
This question is impossible to answer because you don't provide useful
information. First there's a question of your power source and then
there's a question of your load.
You claim you are 200 feet away from the transformer and then talk about
a 1 amp power supply. So do you mean a 1 amp wallwart? You can't put DC
into a transformer so you'd have to rectify it on the output of the
transformer, it would also be a good idea to regulate it. You also don't
state what voltage is acceptable at the load. 12V +/- what? Bare in mind
that wallwart voltage tends to go all over the place depending on the
load and they are unregulated.
14 gauge wire has a resistance of .00297 ohms per foot (assuming copper
wire, and room temperature, resistance goes up with temperature), so 200
feet of it * 500mA gives you about .3V of drop. That means the voltage at
the output of the transformer must be at least .3V above what you need at
the load.
.
- Follow-Ups:
- Re: direct current loss per foot of wire
- From: servozoom
- Re: direct current loss per foot of wire
- Prev by Date: Re: using current to measure a time
- Next by Date: Re: POWER AMPLIFIERS
- Previous by thread: rs232 thermometer
- Next by thread: Re: direct current loss per foot of wire
- Index(es):
Relevant Pages
|