Re: Relay problem



On Fri, 27 Jan 2006 09:04:13 -0800, Chris wrote:
> Rich Grise wrote:
>> On Fri, 27 Jan 2006 21:46:43 +0000, capnfishytakethisout wrote:
>> > This could be OT, but I'm posting here to get replies with no
>> > baggage.... I have a relay in my boiler which buzzes/arcs I'm trying
>> > to diagnose the fault, probably in my wiring. What conditions (eg
>> > shorting) would cause a relay to switch on & off very rapidly (leading
>> > to a buzzing noise) & arc? Many thanks
>> > Jonathan
>>
>> It's ON-topic for s.e.basics, so no worries on that account. The only
>> OFF-topic questions on s.e.b are those that don't involve electrons in
>> one way or another. ;-)
>>
>> I'd look at the physical condition of the relay, like dirt or some
>> obstruction; and check all of the connections in the relay's coil
>> circuit. It sounds like it's not pulling in fully.
>>
>> It used to work, and this symptom appeared recently, right?
>
> Hi, Rich. Always good to hear from you. Nice to see you're spending some
> time amidst us groundlings on s.e.b.

Oh, puh-leeze! I'm a groundling too, just I've been in the trenches for
going on forty years. ;-) (i.e., I've learned the difference from my
elbow to a hole in the ground. I made up that expression by incorporating
two old cliche's[1], by the way. I've heard it on TeeVee. Anyway....

Admittedly, the accolades make my ego get too big for the cubicle, and it
makes me want to dance and shtuff, but please don't gush!

I got a stipend from a benefactor once, (benefactress, actually, but I
don't want to be sexist), and when I went to kiss her feet, she said,
"Oh, don't grovel!" If you want to find somebody to fawn at the feet of,
lurk news:sci.electronics.design for awhile. ;-)

> You're right, it's probably a good idea to look at the physical
> condition of the relay first. Since it's a heating application, I'd
> guess it's probably an AC relay, so I'd also suspect a partial short in
> the coil, or a loose shading ring. Sometimes the shading ring comes
> loose, and can be snapped back into place.
>
> http://www.geindustrial.com/pm/notes/artsci/art02.pdf
>
> Less likely, the thermostat or sensor switch driving the relay might not
> be closing fully, or has gotten resistive.
>
> Best solution might be to replace the relay, and see if that solves the
> problem. If it doesn't, the solution is probably in the switch or
> thermostat.
>
> I hope this does something to improve the knowledge : baggage ratio.
<AOL>
Me, Too!
</AOL> ;-)

Cheers!
Rich
[1] apostrophe used in lieu of accent grave

.



Relevant Pages

  • Re: Relay problem
    ... Rich Grise wrote: ... >> I have a relay in my boiler which buzzes/arcs I'm trying to diagnose the ... the thermostat or sensor switch driving the relay might ...
    (sci.electronics.basics)
  • Re: A/C Compressor Relay will not close
    ... 24 VAC at the contactor, and it doesn't pull in, the coil is NG. ... The tech decided that the circuit board was not working and physically ... I found that the thermostat had been ... relay does not close. ...
    (alt.home.repair)
  • Re: R V QUESTION !! Follow up!
    ... I'd strongly suspect that fan motor relay. ... taking the thermostat out of the circuit. ... It's possible but I don't think it will be the thermal relay. ... Thermostat wires chaffed and shorted together between the thermostat and furnace. ...
    (rec.outdoors.rv-travel)
  • A/C Compressor Relay will not close
    ... The tech decided that the circuit board was not working and physically ... I found that the thermostat had been ... When you set the compressor to start by moving the control ... relay does not close. ...
    (alt.home.repair)
  • Re: 240v Delay Off Timer
    ... stopping for between 3 and 10 mins after the burner has shut down. ... I'm assuming the thermostat switches 24 volts, ... hold the relay energized, ... relay gates the 24 V control voltage to the circulator. ...
    (sci.electronics.design)