Re: How to calculate a battery capacity




Simon Dice wrote:
I'm working on a project in wich I need to have a system running 24hrs
a day , power supply will be solar panels feeding a battery. Can any
one share with me formulas on how to calculate de Amp/hr for the
battery and the power of the solar panel?
Systems will consume average 80watts and need to keep running on a few
clowdy days as well.
Thanks for the assistance!

FYI, it's Amp-hrs (since the units are multiplied), not Amp/hr (which
would be "amps per hour", which is different).

When you divide the amp-hour rating by the battery current (in amps),
you will get how many hours the battery should last. Eg., a 10
Amp-hour battery lasts 10 hours at 1 amp, 5 hours at 2 amps, etc.

As others have said, though, for higher amperages, er, uh, I mean
CURRENTS, the amp-hour value is actually less.

As for the solar panels ... I don't know your specific location, but a
rough calculation gives:

Incident power of sunlight (about 1000 Watts per square meter),
times the efficiency of solar panel (I'll use 12%),
times the fraction of day that panel receives "full sun" (I'll use 6
hours out of 24),
times the fraction of days that are sunny (I'll use 2/3) ***

equals:

(1000 W/m^2) x (0.12) x (6/24) x (2/3) = 20 W/m^2.

The actual, useful power is 20 Watts per square meter. So for an 80W,
24-hour-per-day system, you'd need 4 square meters of solar panel.
That's just a ballpark figure, there are people who know the relevant
numbers better than I do, and you'd need to factor in the efficiency of
charging the battery from the solar panel too.

Hope this helps,

Mark

*** p.s. on the "sunny day" factor: use what is reasonable for your
area. Also, if your area occasionally goes a few days to a week with
rainy weather, you'll need a battery (or several batteries) that can
run for a few days to a week without recharging.

.



Relevant Pages

  • Re: Portable inverter/generator questions
    ... probably a very long cord to locate the generator elsewhere {:-). ... And add a bit more because inverters cost power any way) ... If you only want to run the generator say once every four days, then you need 400+ AmpHours in battery storage. ... j) solar panel regulator so it doesn't pump too much charge into the battery. ...
    (misc.survivalism)
  • Re: solar newbie question
    ... i do not stop by much because i also have a larger boat that i know can ... We only draw battery power to run ... Until now we have used a generator to top off our single ... The best you can do for that amount of money is a 45 watt solar panel kit ...
    (rec.outdoors.rv-travel)
  • Re: Simple (but long) solar charging question
    ... the solar panel hits enough voltage. ... battery from discharging though the solar panel. ... provide in order to charge the battery. ...
    (sci.electronics.basics)
  • Re: solar panel trickle chargins
    ... He says I need 12Volts from the solar panel to charge a 12 volt ... then hook them up to a battery and let them charge ... that the open circuit voltage of solar panels is ...
    (rec.boats.electronics)
  • Re: Simple (but long) solar charging question
    ... There's no way you'll get the circuit above to charge the NiCd ... battery from the solar panel you have. ...
    (sci.electronics.basics)