Re: Power Measuring!! Need Assistance



On Tue, 13 Dec 2005 03:59:28 GMT, Ignoramus12137
<ignoramus12137@xxxxxxxxxxxxxxxxxxxx> wrote:

>On 12 Dec 2005 19:31:51 -0800, @donis <adonis@xxxxxxxxxxx> wrote:
>> Hi Folks, Im working on a power meter design using the ADE7756 and
>> right now im working in the interfacing stage(taking the current and
>> voltage values) . My question is quite simple but right now im a little
>> bit confused. Im my country we use the North American 3-wire
>> configuration we have a Neutral , L1 and L2. From Neutral to ground
>> the voltage is 120VAC
>
>Scary stuff!!!
>
>(hint, that is wrong)
>
>> , L1 to L2 is 240VAC. I know that apparent power
>> equals S=VxI. So far so good with my concepts. My confusion is
>> regardings the power readings.
>
>Be careful applying this rule when you have alternating current. It is
>incorrect to multiply average voltage (RMS) by average current (RMS),
>in case of any but resistive loads.
>
>That is because current may be out of phase with voltage, as it
>happens with motors.
>
>> IF I have a 120V load the current will
>> return thru the Neutral Wire. and if I have a 240 Load the current will
>> return thru one of the lines. My question is if I have both loads
>> connected(120V load and 240V) and S=VxI , what would be my total power
>> value? what voltage should I use for sensing this (120 or 240), what
>> would be the value of my current? would the current value be a
>> vectorial sum? . Please include any information that might help me in
>> my design. Thanks in Advance guys..
>
>I am not sure if you should really be designing a power meter, if you
>are weak on concepts of power etc.
>
>If you have 3 currents, I1, I2, and In (In stands for neutral)
>
>And resistive load
>
>The current In = I1 - I2
>
>110V power is 110*In = 110*(I1-I2)
>220V power is 220*(I1-In) = 220*I2
>
>The sum is Power = 110*(I1-I2) + 220*I2 = 110*(I1+I2)
>

That's only true if the line voltages are symmetric to neutral, which
they never really are. Some domestic electric meters assume this: they
wind both current-sensing coils around a common laminated core, and
use a single potential coil from line-to-line.

It's better to compute power properly,

P = Van * Ia + Vbn * Ib

where the multiplies are instantaneous products, of course.

John


.



Relevant Pages

  • Re: Flyback transformer design confusion!!
    ... When applying a constant DC voltage across a resistive ... load, just *how* can I increase the power into that load, other than by ... Iout is to change the resistor. ...
    (sci.electronics.design)
  • Re: battery charger topology
    ... substantial powers used to charge a 300Ah 24V lead acid battery bank ... normally have to build into the design. ... sets the voltage you must boost to. ... 100KHz may be a bit fast for the power level. ...
    (sci.electronics.design)
  • Re: Power Inverters
    ... The "designer" copied the circuit ... When using a square wave or modified sinewave ... Newer power supplies have built-in power factor correction to make ... the slightly higher voltage won't matter. ...
    (comp.sys.laptops)
  • Re: Flyback transformer design confusion!!
    ... When applying a constant DC voltage across a resistive load, just *how* can I increase the power into that load, other than by changing the resistor? ... only way to change load power if the output voltage remains constant. ...
    (sci.electronics.design)
  • Re: Flyback transformer design confusion!!
    ... would have to calculate the average current flowing through the load. ... and unless something is horribly wrong with your smps, the two should be roughly equal - losses mean the "inductor power" dE*F is somewhat larger than the load power. ... The power given by the expression above is that of the inductance ... its a power supply, so the voltage, by definition, is not supposed to change. ...
    (sci.electronics.design)