Re: .2 volts between neutral and ground



Dave Botsch wrote:

Wouldn't that be from one wire on the outlet, back to breaker box, then
back over the other wire back to the outlet?

So, it sounds like there is more current on one of the neutral, ground
since I last measured (I wonder if hooking up the tv upstairs to the cable
line could have some effect on this).


You have to remember that there is not supposed to be any current
flow in the safety ground, so it will have the same voltage as the
ground buss bar in your breaker box. So, when you connect the meter
between neutral and ground, you are measuring the voltage drop on the
neutral conductor, only. The higher the load on that circuit, whether
at that outlet, or another will show on your meter. Your meter should
have a 10 Megohm input impedance, so the ohm or so resistance of the
ground wire won't affect the reading.


--
Service to my country? Been there, Done that, and I've got my DD214 to
prove it.
Member of DAV #85.

Michael A. Terrell
Central Florida
.



Relevant Pages

  • Re: Carbon dioxide bike tyre inflation (was Re: That was dumb..)
    ... conduit as it's a whole lot easier to pull. ... a Eurostyle terminal strip - you stick the bare end of the wire straight ... circuits radiating from the breaker panel. ... That's after the feed has already passed the meter, ...
    (alt.sysadmin.recovery)
  • Re: Dead Electrical Circuit Troubleshooting
    ... you need to find out what is on this circuit. ... At the circuit breaker: Test the voltage ... ground wire screws in the panel are tight. ... would replace the outlet and use the screw terminals instead. ...
    (alt.home.repair)
  • Re: voltage drop?
    ... My meter is nothing special, will check it against another I have ... Buss bar to main circuit bar ... Dist buss bar to local breaker ... Wire to wire joins in circuit ...
    (alt.coffee)
  • Re: Outting 220 on 110 outlet
    ... Second, You are connecting a hot wire to the ground screw on your outlet, ... At first I thought I had a bad breaker so I held the breaker tight so ...
    (alt.home.repair)
  • Re: HELP me Split 240 to 120
    ... would like to use this power to hook up a home vacuum system. ... to split the 240V line into a 120V outlet for the vacuum itself and the ... black to a new wire out to the outlets at each connection. ... The double breaker in the box says 40 on both connected breakers. ...
    (alt.home.repair)